My TwinCAT PLC project was working fine, but suddenly one day it could not build at all. The error message is simply "The operation could not be completed. Unspecified error".
I also noticed that all my local files, such function block files, would have yellow triangle symbols with an exclamation mark next to them.
If I wanted to start a new project, I would get an exception on _3S.CoDeSys.UserManagement.UserAuthentication.

Girl Spider
  • 330
  • 2
  • 6

1 Answers1

2

After a lot of struggle, I finally fixed the problem, sort of.
Apparently, the problem is related to the FipsAlgorithmPolicy register. The register is used to certify cryptographic software. I am not sure whether it is TwinCAT that is not made to comply with that or my PLC project is not up to that standard.

Anyway, to fix the problem:

Type register editor in Windows Start, right click and choose run as an admin.

In register editor, go to HKEY_LOCAL_MACHINE\System\CurrentControlSet\Control\Lsa.

Under a subkey you should see FipsAlgorithmPolicy. Changed the "enabled" value to 0 or simply delete this register. Restart Visual Studio.

Girl Spider
  • 330
  • 2
  • 6
  • This is a 'known' issue, and something that has been lodged with Beckhoff. They have replicated the issue, and are aiming to include a fix in the next release. of TwinCAT. – Steve Mar 28 '22 at 18:22
  • Thanks for reporting and the fix! I added it to the [known bug list](https://github.com/Roald87/TwinCatChangelog/blob/main/tc3_changelog.md). – Roald Mar 29 '22 at 06:07